This last summer we camped, off-grid, in our early 2015 Unity MB for 6 weeks. We already had 500W of solar but still needed extra battery capacity for the cloudy days. Now that the weather is cooler here in Arizona, it’s a great time to upgrade to lithium. It started with a PM question to SSTraveler which led to a constant correspondence of excellent guidance, and many, many, great suggestions. So this is definitely a joint effort. We are all so fortunate to have Sandy as an anchor to this forum. Her knowledge base and willingness to help others is extraordinary!
I want to document this in detail to help cut the learning curve for others that may wish to take on this project themselves. I'm not a professional electrician. If you do this yourself, I would suggest you do your own research and have your work reviewed by a professional.
I started with a wiring diagram for my road map and updated it as I made changes. The first thing I did was remove all chassis power. I started by disconnecting the solar array. You can cover the panels, or trip the breaker to the solar charger but use a tester to confirm power is not getting to the batteries from your solar panels. Disconnect shore power, flip the generator breaker off, disable generator auto-start if installed, remove the batteries, and also disconnect the lead from the isolation solenoid under the passenger seat to the original battery compartment. It's not really that difficult to remove the seat. There are 4, 11mm bolts that attach the seat. The trick is to swivel the seat to gain better access. It will be easier to remove the isolator relay and connect the cable from the starter battery to the cable going to the DC-DC charger/MPPT discussed later.
Roadmap

I decided to use 2 Lithionics Lithium, 315A batteries for a total of 630AH. They only weigh 68lbs each, are 20.3”L x 6.4”W x 10.0”H, and have an internal Battery Management System plus a heater kit. They are hand-built and tested in Florida and are of great quality. The space below the wardrobe closet seemed like the best place to locate the batteries and most of the wiring. The Victron Multiplus 3000/12, and the Victron SmartSolar 100/50 would be installed in the tall vertical outside rear storage compartment (opposite side of the wardrobe wall).
I removed the two drawers below the closet and the wood divider between the draws for better access. To take the wood divider off, remove the 4 screws on the backside of the divider. Next, remove the 2 right-side metal drawer guides plus the 2 lower wood panels below the drawers. This area is a little cramped and you will need all the space you can get. Next, remove the inverter and the mounting bench. Disconnect the inverter wires. One of the white, 14/2 wires originate from the 15A, entertainment breaker on the WFCO8955 power distribution box by the TV. The other white, 14/2 wire goes to the inverted receptacles. You will eventually need to install a junction box to combine the two wires together. Once the wires are combined, the same 15A breaker will now be the AC source to the previously inverted receptacles. There are 2, 4AWG wires that need to be disconnected from the old inverter. The red one originated from the switched side of the BlueSea Switch (Battery Disconnect) located on the side of the TV cabinet next to the step entry. It originally supplied 12vDC from the house batteries to the inverter. I didn't use it in this upgrade so disconnected it from the switch, then bundle tie the other end with the other wires in the front part of the new battery area. The black 4AWG cable was the inverter ground and originated from the ground lug in the step compartment. I repurposed it to run from the positive busbar in the new battery area to the "OUT" lug on the new Renogy 50A DC-DC charger/MPPT that I located in the old battery step compartment with an 80A ANL inline fuse. I also didn't use the white, thick ground wire that was attached to the old inverter case. When that is done, you still have to rearrange the other wires and remove the flexible heater duct to make room for the new batteries. This is what it looks like when first opened up:
PIC 1,2

The objective is to relocate the wires and heater duct to open up space for the two batteries. This space is only 23" deep. The batteries are 20.3" in length so everything must fit in the front 3" to make space for the new batteries. I removed the heater duct, capped off the exit hole on the heater, and made a new vent through the front cover of the heater which I will cover later in the blog.
PIC 3,4

Bend the propane tubing (see pics above) as close to the heater as possible without actually touching the case. Bend it slowly and carefully so you don't crimp it or cause it to crack. Drill a couple of ½” holes in a low profile junction box and install it on the upright divider between the two bottom panels. Cut off the excess wire from the two 14/2 white covered wire pairs from the old inverter and combine them in the j-box. The wires from the heater will need to be lengthened to move them forward and out of the way too.
I want to document this in detail to help cut the learning curve for others that may wish to take on this project themselves. I'm not a professional electrician. If you do this yourself, I would suggest you do your own research and have your work reviewed by a professional.
I started with a wiring diagram for my road map and updated it as I made changes. The first thing I did was remove all chassis power. I started by disconnecting the solar array. You can cover the panels, or trip the breaker to the solar charger but use a tester to confirm power is not getting to the batteries from your solar panels. Disconnect shore power, flip the generator breaker off, disable generator auto-start if installed, remove the batteries, and also disconnect the lead from the isolation solenoid under the passenger seat to the original battery compartment. It's not really that difficult to remove the seat. There are 4, 11mm bolts that attach the seat. The trick is to swivel the seat to gain better access. It will be easier to remove the isolator relay and connect the cable from the starter battery to the cable going to the DC-DC charger/MPPT discussed later.
Roadmap

I decided to use 2 Lithionics Lithium, 315A batteries for a total of 630AH. They only weigh 68lbs each, are 20.3”L x 6.4”W x 10.0”H, and have an internal Battery Management System plus a heater kit. They are hand-built and tested in Florida and are of great quality. The space below the wardrobe closet seemed like the best place to locate the batteries and most of the wiring. The Victron Multiplus 3000/12, and the Victron SmartSolar 100/50 would be installed in the tall vertical outside rear storage compartment (opposite side of the wardrobe wall).
I removed the two drawers below the closet and the wood divider between the draws for better access. To take the wood divider off, remove the 4 screws on the backside of the divider. Next, remove the 2 right-side metal drawer guides plus the 2 lower wood panels below the drawers. This area is a little cramped and you will need all the space you can get. Next, remove the inverter and the mounting bench. Disconnect the inverter wires. One of the white, 14/2 wires originate from the 15A, entertainment breaker on the WFCO8955 power distribution box by the TV. The other white, 14/2 wire goes to the inverted receptacles. You will eventually need to install a junction box to combine the two wires together. Once the wires are combined, the same 15A breaker will now be the AC source to the previously inverted receptacles. There are 2, 4AWG wires that need to be disconnected from the old inverter. The red one originated from the switched side of the BlueSea Switch (Battery Disconnect) located on the side of the TV cabinet next to the step entry. It originally supplied 12vDC from the house batteries to the inverter. I didn't use it in this upgrade so disconnected it from the switch, then bundle tie the other end with the other wires in the front part of the new battery area. The black 4AWG cable was the inverter ground and originated from the ground lug in the step compartment. I repurposed it to run from the positive busbar in the new battery area to the "OUT" lug on the new Renogy 50A DC-DC charger/MPPT that I located in the old battery step compartment with an 80A ANL inline fuse. I also didn't use the white, thick ground wire that was attached to the old inverter case. When that is done, you still have to rearrange the other wires and remove the flexible heater duct to make room for the new batteries. This is what it looks like when first opened up:
PIC 1,2


The objective is to relocate the wires and heater duct to open up space for the two batteries. This space is only 23" deep. The batteries are 20.3" in length so everything must fit in the front 3" to make space for the new batteries. I removed the heater duct, capped off the exit hole on the heater, and made a new vent through the front cover of the heater which I will cover later in the blog.
PIC 3,4


Bend the propane tubing (see pics above) as close to the heater as possible without actually touching the case. Bend it slowly and carefully so you don't crimp it or cause it to crack. Drill a couple of ½” holes in a low profile junction box and install it on the upright divider between the two bottom panels. Cut off the excess wire from the two 14/2 white covered wire pairs from the old inverter and combine them in the j-box. The wires from the heater will need to be lengthened to move them forward and out of the way too.