Many of the questions you are asking can be answered with a little math.
For example, regarding your inverter wiring/fusing;
Magnum lists a 30 second surge capacity of 3100W for the MS2000 inverter. This would be for starting an AC motor or similar. I feel it would be foolish not to design your system for the maximum output of your inverter.
Your batteries are rated at a max continuous discharge for 50A (100A total). What is the duration of this rating? 5 minutes? 20 minutes? An hour? Since the batteries are rated at 500CCA that means they can surge to at least 500A each for the length of a starting cycle.
V=IxR 3100W@12V with 10% losses is 284Adc I would follow the manufacturer’s recommendation and use a 300A fuse.
You inverter supply wiring is 16ft total on your schematic.
2/0 wire is 0.1mOhm per foot
4/0 wire is 0.06mOhm per foot
Your voltage drop would be as follows (at least).
16x0.1mOhmx289A=0.462V
16x0.06mOhmx289A=0.277V
At 1800W your voltage drop would be .26V (2/0) and .158V (4/0).
It looks like you would be safe with 105C wire at 2/0 with a 300A fuse. Your voltage drops may be an issue due to the small battery size and wire size though. I do not have experience with lithium batteries, so I cannot predict how the battery voltage will sag under load.
All that said, I would stick with 4/0 gauge. It’s not terribly expensive compared to 2/0, and will provide for a more robust system if you decide to add higher load items in the future.
As far as busbars go they are usually rated for continuous current. The max continuous output of the MS2000 is 2100W which is about 200Adc. I don’t see any reason to require a 300A busbar in your application.
Regarding your chassis ground. Charging directly from the alternator REQUIRES the negatives be bonded. Connecting the positives together without a return path for the current will result in zero charging. If you want the grounds isolated most of the time, a high current NO relay could be added between them and triggered by the ignition. The isolator doesn’t need to be connected to the chassis; it can be connected to the negative busbar if you wish. Given that most alternators produce around 13.8-14.1V I do not see any issue with charging your lithium banks directly from the alternator given they have built in BMS. In your case a smart isolator can probably be replaced by a relay triggered from the ignition.
Your shore power plug must be rated for 30A service. If you wish to use 15A service adapters are readily available.
On your USB charging ports you may want to check the parasitic draw. I have seen some that pull 1W when not in use. If that is the case adding a switch to deactivate when not in use would be prudent.
I echo Calbikers concern that you may not have sufficient capacity for your desired usage. You probably have about 80AH usable with your current configuration. Have you done an energy budget for your average day? You may find that you need 150AH or more capacity given your large fridge and induction cooktop usage. The indction cooktop and kettle will easily use 10-15AH each. The fridge could use 50AH+ a day. That puts you are 80AH without counting other consumers.
If you check out this post it seems that the newer alternators are capable of supplying high current levels for charging etc.
https://sprinter-source.com/forums/showpost.php?p=413441&postcount=194
For example, regarding your inverter wiring/fusing;
Magnum lists a 30 second surge capacity of 3100W for the MS2000 inverter. This would be for starting an AC motor or similar. I feel it would be foolish not to design your system for the maximum output of your inverter.
Your batteries are rated at a max continuous discharge for 50A (100A total). What is the duration of this rating? 5 minutes? 20 minutes? An hour? Since the batteries are rated at 500CCA that means they can surge to at least 500A each for the length of a starting cycle.
V=IxR 3100W@12V with 10% losses is 284Adc I would follow the manufacturer’s recommendation and use a 300A fuse.
You inverter supply wiring is 16ft total on your schematic.
2/0 wire is 0.1mOhm per foot
4/0 wire is 0.06mOhm per foot
Your voltage drop would be as follows (at least).
16x0.1mOhmx289A=0.462V
16x0.06mOhmx289A=0.277V
At 1800W your voltage drop would be .26V (2/0) and .158V (4/0).
It looks like you would be safe with 105C wire at 2/0 with a 300A fuse. Your voltage drops may be an issue due to the small battery size and wire size though. I do not have experience with lithium batteries, so I cannot predict how the battery voltage will sag under load.
All that said, I would stick with 4/0 gauge. It’s not terribly expensive compared to 2/0, and will provide for a more robust system if you decide to add higher load items in the future.
As far as busbars go they are usually rated for continuous current. The max continuous output of the MS2000 is 2100W which is about 200Adc. I don’t see any reason to require a 300A busbar in your application.
Regarding your chassis ground. Charging directly from the alternator REQUIRES the negatives be bonded. Connecting the positives together without a return path for the current will result in zero charging. If you want the grounds isolated most of the time, a high current NO relay could be added between them and triggered by the ignition. The isolator doesn’t need to be connected to the chassis; it can be connected to the negative busbar if you wish. Given that most alternators produce around 13.8-14.1V I do not see any issue with charging your lithium banks directly from the alternator given they have built in BMS. In your case a smart isolator can probably be replaced by a relay triggered from the ignition.
Your shore power plug must be rated for 30A service. If you wish to use 15A service adapters are readily available.
On your USB charging ports you may want to check the parasitic draw. I have seen some that pull 1W when not in use. If that is the case adding a switch to deactivate when not in use would be prudent.
I echo Calbikers concern that you may not have sufficient capacity for your desired usage. You probably have about 80AH usable with your current configuration. Have you done an energy budget for your average day? You may find that you need 150AH or more capacity given your large fridge and induction cooktop usage. The indction cooktop and kettle will easily use 10-15AH each. The fridge could use 50AH+ a day. That puts you are 80AH without counting other consumers.
If you check out this post it seems that the newer alternators are capable of supplying high current levels for charging etc.
https://sprinter-source.com/forums/showpost.php?p=413441&postcount=194