Hey guys,

So I have a 3000 watt power inverter. Im trying to figure out how to run the inverter through my 15/20 amp breaker box. I am powering outlets and my water heater through it. Im not too sure how to run this through the box with this set up. Any suggestions?

Heres the inverter:



https://www.walmart.com/ip/PowerDriv...QaApmiEALw_wcB
adam7118 is offline   Reply With Quote
Old 01-25-2020, 02:10 AM   #2
john61ct
 
Join Date: Apr 2018
Posts: 1,763
Thanks: 30
Thanked 419 Times in 358 Posts
Default Re: Inverter to Breaker Box

Convert the input leads of your distribution box to terminate in a 3-prong plug.

Make sure the wiring used is rated to carry more than the maximum possible current over say 50% longer than the actual length.

Power tool extension cable from a reputable hardware shop is a good source, rather than anything Chinese built to a price sold on some sketchy website.

plug that into the inverter outlet.

Ideally secure it so it can't be pulled out accidentally.
john61ct is online now   Reply With Quote
Old 01-25-2020, 03:04 AM   #3
autostaretx
Erratic Member
 
autostaretx's Avatar
 
Join Date: Sep 2006
Location: Seattle
Posts: 18,202
Thanks: 3,179
Thanked 8,335 Times in 6,054 Posts
Default Re: Inverter to Breaker Box

Quote:
Originally Posted by adam7118 View Post
So I have a 3000 watt power inverter. Im trying to figure out how to run the inverter through my 15/20 amp breaker box. I am powering outlets and my water heater through it. Im not too sure how to run this through the box with this set up. Any suggestions?

Heres the inverter:
https://www.walmart.com/ip/PowerDriv...face/372063895
Since the WalMart page doesn't say it's a "pure sine wave" inverter, i would be highly suspicious that it's not.
(in other words, it's a Modified Sine Wave inverter, which some loads will not appreciate).

Next: 3000 watts is 25 amps at 120 volts ... the inverter's individual outlets are not rated for that much current ... they're expecting you to pull a maximum of 15 amps from any one outlet.
I would *carefully* read the manual to check what you can pull from it. You might run one outlet to the water heater, and then use the "put a plug on your breaker box" trick.

If it were me, and i was building a breaker box to come from this inverter, the best way would be to split the bus bars in the box so that half of the breakers are plugged into one of the inverter's sockets, and the other half plug into a different inverter socket (with the manual hinting which ones to use .... one from each side? Or just the upper and lower sockets on one side?

If the inverter provided a 30 amp socket, or provision for "hard wiring" the feed to the breakers, it would be better.

Here's the NEMA socket configurations ... note how the 20 amp socket has a "T" -shaped hole for the "neutral" blade.

NEMA_Female-sockets.png

The typical wall sockets:

NEMAoutlets.jpg

20-amp plugs have a "sideways" neutral blade so that they cannot be plugged into 15-amp sockets.

But even a 20 amp socket is not rated to carry 3000 watts.

--dick
__________________
2005 T1N 118" Freightliner 2500 Passenger Wagon (2.7L, 15" tires, standard (short) roof)
Get YOUR Sprinter's full configuration datacard by entering your VIN to https://www.datamb.com/
http://diysprinter.co.uk/reference <-- lots of service documentation, Thanks to Jens Moller and Arnie_Oli
((as always: this post may go through a couple of post-posting edits... so maybe give it ten minutes before commenting))

Last edited by autostaretx; 01-25-2020 at 03:12 AM.
autostaretx is offline   Reply With Quote
Old 01-25-2020, 03:39 AM   #4
adam7118
 
Join Date: Jan 2020
Posts: 51
Thanks: 0
Thanked 3 Times in 2 Posts
Default Re: Inverter to Breaker Box

Quote:
Originally Posted by autostaretx View Post
Since the WalMart page doesn't say it's a "pure sine wave" inverter, i would be highly suspicious that it's not.
(in other words, it's a Modified Sine Wave inverter, which some loads will not appreciate).

Next: 3000 watts is 25 amps at 120 volts ... the inverter's individual outlets are not rated for that much current ... they're expecting you to pull a maximum of 15 amps from any one outlet.
I would *carefully* read the manual to check what you can pull from it. You might run one outlet to the water heater, and then use the "put a plug on your breaker box" trick.

If it were me, and i was building a breaker box to come from this inverter, the best way would be to split the bus bars in the box so that half of the breakers are plugged into one of the inverter's sockets, and the other half plug into a different inverter socket (with the manual hinting which ones to use .... one from each side? Or just the upper and lower sockets on one side?

If the inverter provided a 30 amp socket, or provision for "hard wiring" the feed to the breakers, it would be better.

Here's the NEMA socket configurations ... note how the 20 amp socket has a "T" -shaped hole for the "neutral" blade.

Attachment 124183

The typical wall sockets:

Attachment 124184

20-amp plugs have a "sideways" neutral blade so that they cannot be plugged into 15-amp sockets.

But even a 20 amp socket is not rated to carry 3000 watts.

--dick
I believe you're right. This is what it says in the manual.. This is disheartening. But it sounds like splitting the bus bars would be the way to go

Name PD3000 Input 11−15V DC Output 115V AC Output Waveform Modified Sine Wave (MSW) Continuous Power 3000 Watt Surge Power 6000 Watt Efficiency MAX 88% Power Switch ON/OFF Control ≤ 1A DC No Load Draw 11
adam7118 is offline   Reply With Quote
Old 01-25-2020, 03:47 AM   #5
OrioN
2008 2500 170" EXT
 
OrioN's Avatar
 
Join Date: Sep 2007
Location: Vancouver, BC
Posts: 11,032
Thanks: 619
Thanked 2,738 Times in 1,999 Posts
Default Re: Inverter to Breaker Box

It is possible that the two outlets are 15A each.... And not a single duplex one.
OrioN is offline   Reply With Quote
Old 01-25-2020, 02:13 PM   #6
adam7118
 
Join Date: Jan 2020
Posts: 51
Thanks: 0
Thanked 3 Times in 2 Posts
Default Re: Inverter to Breaker Box

Quote:
Originally Posted by OrioN View Post
It is possible that the two outlets are 15A each.... And not a single duplex one.
How would I figure that out?
adam7118 is offline   Reply With Quote
Old 01-25-2020, 02:33 PM   #7
adam7118
 
Join Date: Jan 2020
Posts: 51
Thanks: 0
Thanked 3 Times in 2 Posts
Default Re: Inverter to Breaker Box

Also, there are four outlets on the front of this
adam7118 is offline   Reply With Quote
Old 01-25-2020, 04:01 PM   #8
HarryN
 
Join Date: May 2010
Location: Pleasanton, CA
Posts: 2,608
Thanks: 628
Thanked 839 Times in 685 Posts
Default Re: Inverter to Breaker Box

https://www.solar-electric.com/outba...-vfx2812m.html

https://www.solar-electric.com/lib/w...obilespecs.pdf

Just as a point of comparison, this is what a ~ 3000 watt inverter looks like.

Unfortunately there is a lot of fraud in the inverter market.

If you would like to use that inverter for your project, a single 15 or 20 amp breaker should be sufficient to protect 10 awg wire in your van.

Just wire your van the same way that a home 15 or 20 amp circuit is done.

Plan to run 1 appliance at a time.
__________________
Power systems for conversion vans and emergency preparedness.

https://wirlnet-inc.square.site
HarryN is offline   Reply With Quote
Old 01-25-2020, 05:05 PM   #9
AirJoseph
 
AirJoseph's Avatar
 
Join Date: May 2018
Location: Lost Wages Nevada
Posts: 583
Thanks: 137
Thanked 71 Times in 58 Posts
Default Re: Inverter to Breaker Box

Quote:
Originally Posted by adam7118 View Post
How would I figure that out?
A meter would be your friend here.

The manual says that each of the four receptacles is rated for 15 amps so they must be fused individually. No need for a breaker box in this case.

You could possibly parallel connect two outlets to one phase of the panel but I wouldn't risk it.

Last edited by AirJoseph; 01-25-2020 at 05:12 PM.
AirJoseph is offline   Reply With Quote
Old 01-25-2020, 05:56 PM   #10
autostaretx
Erratic Member
 
autostaretx's Avatar
 
Join Date: Sep 2006
Location: Seattle
Posts: 18,202
Thanks: 3,179
Thanked 8,335 Times in 6,054 Posts
Default Re: Inverter to Breaker Box

Quote:
Originally Posted by OrioN View Post
It is possible that the two outlets are 15A each.... And not a single duplex one.
Based upon the photo:

PD3000.jpeg

See the "crease" running across the front between the outlets?
(plus, on 3rd viewing, each side's outlets are not vertically aligned)

That tells me that each outlet is individually wired to the internal circuitry.
So each outlet is capable of 15 amps. They're not a "mated pair" like a typical duplex outlet.

Whether or not the *internal* circuitry can handle "all 25 amps" on one side (and this inverter has 100% surge allowance ... 50 amp spikes!) can't be determined without opening it up.

Adam's "expanded" listing of the inverter's specs also clearly state that it's an MSW unit.
That means that, instead of a sine wave, this is what your plugged-in gadgetry will be getting:

microwaveTraces.jpg

(photo of oscilloscope looking at my own 1kw MSW inverter's output)
((i'm pretty sure it damaged my microwave))

--dick
__________________
2005 T1N 118" Freightliner 2500 Passenger Wagon (2.7L, 15" tires, standard (short) roof)
Get YOUR Sprinter's full configuration datacard by entering your VIN to https://www.datamb.com/
http://diysprinter.co.uk/reference <-- lots of service documentation, Thanks to Jens Moller and Arnie_Oli
((as always: this post may go through a couple of post-posting edits... so maybe give it ten minutes before commenting))

Last edited by autostaretx; 01-25-2020 at 06:03 PM.
autostaretx is offline   Reply With Quote
The Following User Says Thank You to autostaretx For This Useful Post:
HarryN (01-25-2020)

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump



All times are GMT. The time now is 12:13 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2020, vBulletin Solutions, Inc.